 Post subject: Water Heater Question
PostPosted: Wed Apr 02, 2025 9:20 am 
Offline
User avatar

Joined: Mon May 02, 2011 4:29 pm
Posts: 41185
Location: Everywhere
pizza_Place: giordanos
I have a question about the water heater situation at my kid's new home. The heating unit is only two years old and when the gas guy came to turn on gas and check everything all is working.

He turned off the water heater though and said it cannot be turned back on until an issue with the venting is fixed. He said the venting pipe above the water heater was getting too warm and there wasn't the correct draft.

The house was inspected and as far as we can tell the chimney and all other thing are fine. I have not heard of such a thing on the water heater exhaust before. Any one hear have a Darko level of insight?

_________________
Elections have consequences.


Top
 Profile  
 
PostPosted: Wed Apr 02, 2025 9:22 am 
Offline
User avatar

Joined: Tue Aug 19, 2008 3:03 pm
Posts: 44067
Go tankless

_________________
Juice's Lecture Notes wrote:
I am not a legal expert, how many times do I have to say it?


Top
 Profile  
 
PostPosted: Wed Apr 02, 2025 10:08 am 
Offline
User avatar

Joined: Wed Jun 28, 2006 9:29 am
Posts: 66206
Location: Darkside Estates
pizza_Place: A cat got an online degree.
I'm assuming this is an atmospheric (natural draft, metal flue pipe)?

_________________
"Play until it hurts, then play until it hurts to not play."
http://soundcloud.com/darkside124 HOF 2013, MM Champion 2014
bigfan wrote:
Many that is true, but an incomplete statement.


Top
 Profile  
 
PostPosted: Wed Apr 02, 2025 10:43 am 
Offline
User avatar

Joined: Mon May 02, 2011 4:29 pm
Posts: 41185
Location: Everywhere
pizza_Place: giordanos
Darkside wrote:
I'm assuming this is an atmospheric (natural draft, metal flue pipe)?


Yes standard gray pipe sitting atop the water heater that then goes up angles then into the brick wall/chimney structure.

_________________
Elections have consequences.


Top
 Profile  
 
PostPosted: Wed Apr 02, 2025 10:46 am 
Offline
User avatar

Joined: Thu Jun 22, 2006 3:55 pm
Posts: 33534
Location: Wrigley
pizza_Place: Warren Buffet of Cock
pittmike wrote:
Darkside wrote:
I'm assuming this is an atmospheric (natural draft, metal flue pipe)?


Yes standard gray pipe sitting atop the water heater that then goes up angles then into the brick wall/chimney structure.


brick wall, problem identified. Must be a stubborn water heater.

_________________
Hawaii (fuck) You


Top
 Profile  
 
PostPosted: Wed Apr 02, 2025 10:52 am 
Offline
User avatar

Joined: Mon May 02, 2011 4:29 pm
Posts: 41185
Location: Everywhere
pizza_Place: giordanos
denisdman wrote:
pittmike wrote:
Darkside wrote:
I'm assuming this is an atmospheric (natural draft, metal flue pipe)?


Yes standard gray pipe sitting atop the water heater that then goes up angles then into the brick wall/chimney structure.


brick wall, problem identified. Must be a stubborn water heater.


yup

_________________
Elections have consequences.


Top
 Profile  
 
PostPosted: Wed Apr 02, 2025 11:23 am 
Offline
User avatar

Joined: Wed Jun 28, 2006 9:29 am
Posts: 66206
Location: Darkside Estates
pizza_Place: A cat got an online degree.
pittmike wrote:
Darkside wrote:
I'm assuming this is an atmospheric (natural draft, metal flue pipe)?


Yes standard gray pipe sitting atop the water heater that then goes up angles then into the brick wall/chimney structure.

The heat isn't a problem. It should be 350+ degree exhaust. The draft pressure is important though. Normally i drill a small hole in the flue pipe and use a draft gauge or a manometer to measure the draft pressure. Minimum should be 0.01 inches of water column pressure. If it doesn't do that there's yiur problem.

_________________
"Play until it hurts, then play until it hurts to not play."
http://soundcloud.com/darkside124 HOF 2013, MM Champion 2014
bigfan wrote:
Many that is true, but an incomplete statement.


Top
 Profile  
 
PostPosted: Wed Apr 02, 2025 11:25 am 
Offline
User avatar

Joined: Mon May 02, 2011 4:29 pm
Posts: 41185
Location: Everywhere
pizza_Place: giordanos
Darkside wrote:
pittmike wrote:
Darkside wrote:
I'm assuming this is an atmospheric (natural draft, metal flue pipe)?


Yes standard gray pipe sitting atop the water heater that then goes up angles then into the brick wall/chimney structure.

The heat isn't a problem. It should be 350+ degree exhaust. The draft pressure is important though. Normally i drill a small hole in the flue pipe and use a draft gauge or a manometer to measure the draft pressure. Minimum should be 0.01 inches of water column pressure. If it doesn't do that there's yiur problem.


Thanks

_________________
Elections have consequences.


Top
 Profile  
 
PostPosted: Wed Apr 02, 2025 11:58 am 
Offline
User avatar

Joined: Sun Aug 21, 2016 3:24 pm
Posts: 17447
pizza_Place: Pequods
Darkside wrote:
pittmike wrote:
Darkside wrote:
I'm assuming this is an atmospheric (natural draft, metal flue pipe)?


Yes standard gray pipe sitting atop the water heater that then goes up angles then into the brick wall/chimney structure.

The heat isn't a problem. It should be 350+ degree exhaust. The draft pressure is important though. Normally i drill a small hole in the flue pipe and use a draft gauge or a manometer to measure the draft pressure. Minimum should be 0.01 inches of water column pressure. If it doesn't do that there's yiur problem.

Where did you get the manometer?

_________________
“When I walked in this morning, and saw the flag was at half mast, I thought 'alright another bureaucrat ate it.'" - Ron Swanson


Top
 Profile  
 
PostPosted: Wed Apr 02, 2025 12:00 pm 
Offline
User avatar

Joined: Mon May 02, 2011 4:29 pm
Posts: 41185
Location: Everywhere
pizza_Place: giordanos
Ogie Oglethorpe wrote:
Darkside wrote:
pittmike wrote:
Darkside wrote:
I'm assuming this is an atmospheric (natural draft, metal flue pipe)?


Yes standard gray pipe sitting atop the water heater that then goes up angles then into the brick wall/chimney structure.

The heat isn't a problem. It should be 350+ degree exhaust. The draft pressure is important though. Normally i drill a small hole in the flue pipe and use a draft gauge or a manometer to measure the draft pressure. Minimum should be 0.01 inches of water column pressure. If it doesn't do that there's yiur problem.

Where did you get the manometer?


Manhattan

_________________
Elections have consequences.


Top
 Profile  
 
PostPosted: Wed Apr 02, 2025 12:15 pm 
Offline
User avatar

Joined: Wed Jun 28, 2006 9:29 am
Posts: 66206
Location: Darkside Estates
pizza_Place: A cat got an online degree.
pittmike wrote:
Ogie Oglethorpe wrote:
Darkside wrote:
pittmike wrote:
Darkside wrote:
I'm assuming this is an atmospheric (natural draft, metal flue pipe)?


Yes standard gray pipe sitting atop the water heater that then goes up angles then into the brick wall/chimney structure.

The heat isn't a problem. It should be 350+ degree exhaust. The draft pressure is important though. Normally i drill a small hole in the flue pipe and use a draft gauge or a manometer to measure the draft pressure. Minimum should be 0.01 inches of water column pressure. If it doesn't do that there's yiur problem.

Where did you get the manometer?


Manhattan

Isle of Mann.

_________________
"Play until it hurts, then play until it hurts to not play."
http://soundcloud.com/darkside124 HOF 2013, MM Champion 2014
bigfan wrote:
Many that is true, but an incomplete statement.


Top
 Profile  
 
PostPosted: Wed Apr 02, 2025 12:55 pm 
Offline
User avatar

Joined: Mon May 14, 2018 6:47 am
Posts: 1222
pizza_Place: Bennys
pittmike wrote:
Darkside wrote:
pittmike wrote:
Darkside wrote:
I'm assuming this is an atmospheric (natural draft, metal flue pipe)?


Yes standard gray pipe sitting atop the water heater that then goes up angles then into the brick wall/chimney structure.

The heat isn't a problem. It should be 350+ degree exhaust. The draft pressure is important though. Normally i drill a small hole in the flue pipe and use a draft gauge or a manometer to measure the draft pressure. Minimum should be 0.01 inches of water column pressure. If it doesn't do that there's yiur problem.


Thanks

If he can, go on the roof and pull the cap off to check for blockage. I had these tiny chimney swifts that managed to squeeze through the screen and nest in mine. My CO detectors never went off and was still venting I guess. My only sign was a tiny drip at the base of the flue pipe.

_________________
rogers park bryan wrote:
Mulli is Howard Stern in his prime compared to Haugh.


Top
 Profile  
 
PostPosted: Wed Apr 02, 2025 1:15 pm 
Offline
User avatar

Joined: Thu Jun 22, 2006 3:55 pm
Posts: 33534
Location: Wrigley
pizza_Place: Warren Buffet of Cock
Oh the irony of “The Man” chiming in amid all the Man jokes….

_________________
Hawaii (fuck) You


Top
 Profile  
 
PostPosted: Thu Apr 03, 2025 8:03 am 
Offline
User avatar

Joined: Thu Feb 17, 2005 2:35 pm
Posts: 83313
turn it on and sit next to it for a few hours, just to test out the venting

if there is a fire, try to die in it, as best you can

_________________
O judgment! Thou art fled to brutish beasts,
And men have lost their reason.


Top
 Profile  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 14 posts ] 

All times are UTC - 6 hours [ DST ]


Who is online

Users browsing this forum: Google [Bot] and 2 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum

Search for:
Jump to:  
Powered by phpBB® Forum Software © phpBB Group