I have just been informed that our furnace is continually blowing cold air. The fan continues to run even when the thermostat it shut off. I had my wife flip of the “light switch” on the side of the furnace and that did shut off the fan. The thermostat is one of those cheap round mechanical style and the furnace is a high efficiency unit that is at least 20 years old. Of course I am in the process of flying back from Denver so I can’t view it 1st hand until this evening. I can do basic tests and repairs but obviously if this is serious it will require an expert. I’m just not sure whether to just have my wife call a technician now or hold off until I can mess with it a bit tonight. Any thoughts or suggestions (other than move)? Thanks in advance.

_________________
“Mr. Trump is unfit for our nation’s highest office.”- JD Vance
“My god, what an !diot.”- JD Vance tweet on Trump
“I’m a ‘Never Trump’ guy”- JD Vance


Top
 Profile  
 
PostPosted: Thu Jan 16, 2020 2:08 pm 
Offline
User avatar

Joined: Tue Aug 19, 2008 3:03 pm
Posts: 43582
Stay in a warm hotel tonight and let your wife handle it.

_________________
Juice's Lecture Notes wrote:
I am not a legal expert, how many times do I have to say it?


Top
 Profile  
 
PostPosted: Thu Jan 16, 2020 2:09 pm 
Offline
User avatar

Joined: Wed Jun 28, 2006 9:29 am
Posts: 65791
Location: Darkside Estates
pizza_Place: A cat got an online degree.
Zippy-The-Pinhead wrote:
I have just been informed that our furnace is continually blowing cold air. The fan continues to run even when the thermostat it shut off. I had my wife flip of the “light switch” on the side of the furnace and that did shut off the fan. The thermostat is one of those cheap round mechanical style and the furnace is a high efficiency unit that is at least 20 years old. Of course I am in the process of flying back from Denver so I can’t view it 1st hand until this evening. I can do basic tests and repairs but obviously if this is serious it will require an expert. I’m just not sure whether to just have my wife call a technician now or hold off until I can mess with it a bit tonight. Any thoughts or suggestions (other than move)? Thanks in advance.

If the heat comes on when you turn up the stat it may be that the thermostat is sending an improper signal to the furnace to run. You can test this with a multimeter. If you have voltage between the g and the c terminal 24 volts it's probably a thermostat thing.
If the heat won't come on but the fan stays on it's likely an open limit. Either a main limit or possibly an auxiliary limit in a blower compartment. If you put your meter on both sides of the limit and it reads 0 its closed and not likely the cause. If you read 24 volts across a limit its open and that's the problem.
If it's a high efficiency it should have an error code should there be a reason other than the thermostat that's causing the issue. Before killing power to the furnace see if its throwing a code. You can update this thread with a make and model and I'll try to help.

_________________
"Play until it hurts, then play until it hurts to not play."
http://soundcloud.com/darkside124 HOF 2013, MM Champion 2014
bigfan wrote:
Many that is true, but an incomplete statement.


Top
 Profile  
 
PostPosted: Thu Jan 16, 2020 2:15 pm 
Offline
100000 CLUB
User avatar

Joined: Wed Feb 08, 2006 6:17 pm
Posts: 102657
pizza_Place: Vito & Nick's
Go tankless.

_________________
Joe Orr Road Rod wrote:
It's more fun to be a victim
Caller Bob wrote:
There will never be an effective vaccine. I'll never get one anyway.


Top
 Profile  
 
PostPosted: Thu Jan 16, 2020 2:16 pm 
Offline
User avatar

Joined: Mon Oct 03, 2005 1:04 pm
Posts: 13260
Location: God's country
pizza_Place: Gem City
Darkside wrote:
Zippy-The-Pinhead wrote:
I have just been informed that our furnace is continually blowing cold air. The fan continues to run even when the thermostat it shut off. I had my wife flip of the “light switch” on the side of the furnace and that did shut off the fan. The thermostat is one of those cheap round mechanical style and the furnace is a high efficiency unit that is at least 20 years old. Of course I am in the process of flying back from Denver so I can’t view it 1st hand until this evening. I can do basic tests and repairs but obviously if this is serious it will require an expert. I’m just not sure whether to just have my wife call a technician now or hold off until I can mess with it a bit tonight. Any thoughts or suggestions (other than move)? Thanks in advance.

If the heat comes on when you turn up the stat it may be that the thermostat is sending an improper signal to the furnace to run. You can test this with a multimeter. If you have voltage between the g and the c terminal 24 volts it's probably a thermostat thing.
If the heat won't come on but the fan stays on it's likely an open limit. Either a main limit or possibly an auxiliary limit in a blower compartment. If you put your meter on both sides of the limit and it reads 0 its closed and not likely the cause. If you read 24 volts across a limit its open and that's the problem.
If it's a high efficiency it should have an error code should there be a reason other than the thermostat that's causing the issue. Before killing power to the furnace see if its throwing a code. You can update this thread with a make and model and I'll try to help.

Thanks, will do.

_________________
“Mr. Trump is unfit for our nation’s highest office.”- JD Vance
“My god, what an !diot.”- JD Vance tweet on Trump
“I’m a ‘Never Trump’ guy”- JD Vance


Top
 Profile  
 
PostPosted: Thu Jan 16, 2020 2:18 pm 
Offline
User avatar

Joined: Thu Sep 03, 2015 6:55 am
Posts: 6549
pizza_Place: Giordano's
Move


Top
 Profile  
 
PostPosted: Thu Jan 16, 2020 2:20 pm 
Offline
User avatar

Joined: Wed Jun 21, 2006 6:57 pm
Posts: 92106
Location: To the left of my post
Zippy-The-Pinhead wrote:
I have just been informed that our furnace is continually blowing cold air.
I think that's called an air conditioner.

_________________
You do not talk to me like that! I work too hard to deal with this stuff! I work too hard! I'm an important member of the CSFMB! I drive a Dodge Stratus!


Top
 Profile  
 
PostPosted: Thu Jan 16, 2020 2:22 pm 
Offline
100000 CLUB
User avatar

Joined: Wed Feb 08, 2006 6:17 pm
Posts: 102657
pizza_Place: Vito & Nick's
Boilermaker Rick wrote:
Zippy-The-Pinhead wrote:
I have just been informed that our furnace is continually blowing cold air.
I think that's called an air conditioner.
:lol:

Yeah Zippy. Tell your wife to turn the AC off, and start making a pie.

_________________
Joe Orr Road Rod wrote:
It's more fun to be a victim
Caller Bob wrote:
There will never be an effective vaccine. I'll never get one anyway.


Top
 Profile  
 
PostPosted: Thu Jan 16, 2020 2:26 pm 
Offline
User avatar

Joined: Tue Nov 05, 2019 11:08 am
Posts: 9
pizza_Place: Pizza Hut
What is your approach to combustion safety?

_________________
1-800-HEATING


Top
 Profile  
 
PostPosted: Thu Jan 16, 2020 2:33 pm 
Offline
User avatar

Joined: Thu Feb 14, 2013 2:12 pm
Posts: 2865
pizza_Place: maciano's
HVAC / water heater... what’s the difference.

Should I change the anode rod in my water heater?


Top
 Profile  
 
PostPosted: Thu Jan 16, 2020 2:37 pm 
Offline
100000 CLUB
User avatar

Joined: Wed Feb 08, 2006 6:17 pm
Posts: 102657
pizza_Place: Vito & Nick's
How about the johnson rod on your SAAB?

_________________
Joe Orr Road Rod wrote:
It's more fun to be a victim
Caller Bob wrote:
There will never be an effective vaccine. I'll never get one anyway.


Top
 Profile  
 
PostPosted: Thu Jan 16, 2020 9:07 pm 
Offline
User avatar

Joined: Mon Oct 03, 2005 1:04 pm
Posts: 13260
Location: God's country
pizza_Place: Gem City
Darkside wrote:
Zippy-The-Pinhead wrote:
I have just been informed that our furnace is continually blowing cold air. The fan continues to run even when the thermostat it shut off. I had my wife flip of the “light switch” on the side of the furnace and that did shut off the fan. The thermostat is one of those cheap round mechanical style and the furnace is a high efficiency unit that is at least 20 years old. Of course I am in the process of flying back from Denver so I can’t view it 1st hand until this evening. I can do basic tests and repairs but obviously if this is serious it will require an expert. I’m just not sure whether to just have my wife call a technician now or hold off until I can mess with it a bit tonight. Any thoughts or suggestions (other than move)? Thanks in advance.

If the heat comes on when you turn up the stat it may be that the thermostat is sending an improper signal to the furnace to run. You can test this with a multimeter. If you have voltage between the g and the c terminal 24 volts it's probably a thermostat thing.
If the heat won't come on but the fan stays on it's likely an open limit. Either a main limit or possibly an auxiliary limit in a blower compartment. If you put your meter on both sides of the limit and it reads 0 its closed and not likely the cause. If you read 24 volts across a limit its open and that's the problem.
If it's a high efficiency it should have an error code should there be a reason other than the thermostat that's causing the issue. Before killing power to the furnace see if its throwing a code. You can update this thread with a make and model and I'll try to help.
So I had to reset the flame rollout switch. That seems to have at least temporarily solved the problem. The furnace has been running for about 1/2 an hour and the house is finally nearing “room temperature “. I also pulled the limit switch to make sure it wasn’t stuck and that solved the fan running problem. The question now is: is this a bigger concern even if it doesn’t happen again?

Thanks again btw. :salut:

_________________
“Mr. Trump is unfit for our nation’s highest office.”- JD Vance
“My god, what an !diot.”- JD Vance tweet on Trump
“I’m a ‘Never Trump’ guy”- JD Vance


Top
 Profile  
 
PostPosted: Thu Jan 16, 2020 11:13 pm 
Offline
User avatar

Joined: Thu Jul 13, 2006 1:25 pm
Posts: 27055
It'll happen again. The flame rollout switch means the flue is backing up or there is oxygen mixing post oriface which indicates a cracked heat exchanger. You'll either be cleaning out a bird nest or replacing the whole furnace. There's a small chance the switch itself is just failing but pretty unlikely.

_________________
the world will always the world. your entire existence is defined by your response.


Top
 Profile  
 
PostPosted: Thu Jan 16, 2020 11:29 pm 
Offline
User avatar

Joined: Wed Jun 28, 2006 9:29 am
Posts: 65791
Location: Darkside Estates
pizza_Place: A cat got an online degree.
Zippy-The-Pinhead wrote:
Darkside wrote:
Zippy-The-Pinhead wrote:
I have just been informed that our furnace is continually blowing cold air. The fan continues to run even when the thermostat it shut off. I had my wife flip of the “light switch” on the side of the furnace and that did shut off the fan. The thermostat is one of those cheap round mechanical style and the furnace is a high efficiency unit that is at least 20 years old. Of course I am in the process of flying back from Denver so I can’t view it 1st hand until this evening. I can do basic tests and repairs but obviously if this is serious it will require an expert. I’m just not sure whether to just have my wife call a technician now or hold off until I can mess with it a bit tonight. Any thoughts or suggestions (other than move)? Thanks in advance.

If the heat comes on when you turn up the stat it may be that the thermostat is sending an improper signal to the furnace to run. You can test this with a multimeter. If you have voltage between the g and the c terminal 24 volts it's probably a thermostat thing.
If the heat won't come on but the fan stays on it's likely an open limit. Either a main limit or possibly an auxiliary limit in a blower compartment. If you put your meter on both sides of the limit and it reads 0 its closed and not likely the cause. If you read 24 volts across a limit its open and that's the problem.
If it's a high efficiency it should have an error code should there be a reason other than the thermostat that's causing the issue. Before killing power to the furnace see if its throwing a code. You can update this thread with a make and model and I'll try to help.
So I had to reset the flame rollout switch. That seems to have at least temporarily solved the problem. The furnace has been running for about 1/2 an hour and the house is finally nearing “room temperature “. I also pulled the limit switch to make sure it wasn’t stuck and that solved the fan running problem. The question now is: is this a bigger concern even if it doesn’t happen again?

Thanks again btw. :salut:

Rollout switches indicate either a lack of combustion air or a bad heat exchanger typically.
So... you can take the intake pipe off the furnace and see if that helps. It could be a clogged intake pipe.
If it's a bad or rusted out secondary heat exchanger you would confirm with a combustion analysis. High co and low o2 is likely what you'd find.
One way to test an intake pipe is to drop a golf ball into the intake from outside. The pipes should be pitched toward the furnace so if the ball makes it back to the furnace that confirms the pitch is correct and the pipe is clear. Exhaust should be the same way.
Also I've seen clogged condensate traps cause this. If water is backing up into the secondary it could be enough to cause a rollout to trip but typically the pressure switch won't close before that happens but I've seen it before so I wouldn't rule it out entirely.

_________________
"Play until it hurts, then play until it hurts to not play."
http://soundcloud.com/darkside124 HOF 2013, MM Champion 2014
bigfan wrote:
Many that is true, but an incomplete statement.


Top
 Profile  
 
PostPosted: Thu Jan 16, 2020 11:31 pm 
Offline
User avatar

Joined: Wed Jun 28, 2006 9:29 am
Posts: 65791
Location: Darkside Estates
pizza_Place: A cat got an online degree.
Also.... is this a carrier?

Aorrybit took so long to get back to you I'm out working.

_________________
"Play until it hurts, then play until it hurts to not play."
http://soundcloud.com/darkside124 HOF 2013, MM Champion 2014
bigfan wrote:
Many that is true, but an incomplete statement.


Top
 Profile  
 
PostPosted: Thu Jan 16, 2020 11:40 pm 
Offline
User avatar

Joined: Thu Jul 13, 2006 1:25 pm
Posts: 27055
Darkside wrote:
Zippy-The-Pinhead wrote:
Darkside wrote:
Zippy-The-Pinhead wrote:
I have just been informed that our furnace is continually blowing cold air. The fan continues to run even when the thermostat it shut off. I had my wife flip of the “light switch” on the side of the furnace and that did shut off the fan. The thermostat is one of those cheap round mechanical style and the furnace is a high efficiency unit that is at least 20 years old. Of course I am in the process of flying back from Denver so I can’t view it 1st hand until this evening. I can do basic tests and repairs but obviously if this is serious it will require an expert. I’m just not sure whether to just have my wife call a technician now or hold off until I can mess with it a bit tonight. Any thoughts or suggestions (other than move)? Thanks in advance.

If the heat comes on when you turn up the stat it may be that the thermostat is sending an improper signal to the furnace to run. You can test this with a multimeter. If you have voltage between the g and the c terminal 24 volts it's probably a thermostat thing.
If the heat won't come on but the fan stays on it's likely an open limit. Either a main limit or possibly an auxiliary limit in a blower compartment. If you put your meter on both sides of the limit and it reads 0 its closed and not likely the cause. If you read 24 volts across a limit its open and that's the problem.
If it's a high efficiency it should have an error code should there be a reason other than the thermostat that's causing the issue. Before killing power to the furnace see if its throwing a code. You can update this thread with a make and model and I'll try to help.
So I had to reset the flame rollout switch. That seems to have at least temporarily solved the problem. The furnace has been running for about 1/2 an hour and the house is finally nearing “room temperature “. I also pulled the limit switch to make sure it wasn’t stuck and that solved the fan running problem. The question now is: is this a bigger concern even if it doesn’t happen again?

Thanks again btw. :salut:

Rollout switches indicate either a lack of combustion air or a bad heat exchanger typically.
So... you can take the intake pipe off the furnace and see if that helps. It could be a clogged intake pipe.
If it's a bad or rusted out secondary heat exchanger you would confirm with a combustion analysis. High co and low o2 is likely what you'd find.
One way to test an intake pipe is to drop a golf ball into the intake from outside. The pipes should be pitched toward the furnace so if the ball makes it back to the furnace that confirms the pitch is correct and the pipe is clear. Exhaust should be the same way.
Also I've seen clogged condensate traps cause this. If water is backing up into the secondary it could be enough to cause a rollout to trip but typically the pressure switch won't close before that happens but I've seen it before so I wouldn't rule it out entirely.


To check intake just run the furnace without the cover on the burner. Might have to tape down a door switch.

_________________
the world will always the world. your entire existence is defined by your response.


Top
 Profile  
 
PostPosted: Thu Jan 16, 2020 11:51 pm 
Offline
User avatar

Joined: Wed Jun 28, 2006 9:29 am
Posts: 65791
Location: Darkside Estates
pizza_Place: A cat got an online degree.
IkeSouth wrote:
Darkside wrote:
Zippy-The-Pinhead wrote:
Darkside wrote:
Zippy-The-Pinhead wrote:
I have just been informed that our furnace is continually blowing cold air. The fan continues to run even when the thermostat it shut off. I had my wife flip of the “light switch” on the side of the furnace and that did shut off the fan. The thermostat is one of those cheap round mechanical style and the furnace is a high efficiency unit that is at least 20 years old. Of course I am in the process of flying back from Denver so I can’t view it 1st hand until this evening. I can do basic tests and repairs but obviously if this is serious it will require an expert. I’m just not sure whether to just have my wife call a technician now or hold off until I can mess with it a bit tonight. Any thoughts or suggestions (other than move)? Thanks in advance.

If the heat comes on when you turn up the stat it may be that the thermostat is sending an improper signal to the furnace to run. You can test this with a multimeter. If you have voltage between the g and the c terminal 24 volts it's probably a thermostat thing.
If the heat won't come on but the fan stays on it's likely an open limit. Either a main limit or possibly an auxiliary limit in a blower compartment. If you put your meter on both sides of the limit and it reads 0 its closed and not likely the cause. If you read 24 volts across a limit its open and that's the problem.
If it's a high efficiency it should have an error code should there be a reason other than the thermostat that's causing the issue. Before killing power to the furnace see if its throwing a code. You can update this thread with a make and model and I'll try to help.
So I had to reset the flame rollout switch. That seems to have at least temporarily solved the problem. The furnace has been running for about 1/2 an hour and the house is finally nearing “room temperature “. I also pulled the limit switch to make sure it wasn’t stuck and that solved the fan running problem. The question now is: is this a bigger concern even if it doesn’t happen again?

Thanks again btw. :salut:

Rollout switches indicate either a lack of combustion air or a bad heat exchanger typically.
So... you can take the intake pipe off the furnace and see if that helps. It could be a clogged intake pipe.
If it's a bad or rusted out secondary heat exchanger you would confirm with a combustion analysis. High co and low o2 is likely what you'd find.
One way to test an intake pipe is to drop a golf ball into the intake from outside. The pipes should be pitched toward the furnace so if the ball makes it back to the furnace that confirms the pitch is correct and the pipe is clear. Exhaust should be the same way.
Also I've seen clogged condensate traps cause this. If water is backing up into the secondary it could be enough to cause a rollout to trip but typically the pressure switch won't close before that happens but I've seen it before so I wouldn't rule it out entirely.


To check intake just run the furnace without the cover on the burner. Might have to tape down a door switch.

This will likely cause other problems. Best practice is to cut the intake pipe a foot or so away from the furnace move the pipe ends apart and leave the combustion door in place. The pipe can be put back together easily enough with a fernco or glue in a coupling.

_________________
"Play until it hurts, then play until it hurts to not play."
http://soundcloud.com/darkside124 HOF 2013, MM Champion 2014
bigfan wrote:
Many that is true, but an incomplete statement.


Top
 Profile  
 
PostPosted: Fri Jan 17, 2020 1:24 am 
Offline

Joined: Tue Jun 01, 2010 1:12 pm
Posts: 8642
pizza_Place: Passero's
Darkside wrote:
I'm out working.



at 11:30PM?

_________________
rogers park bryan wrote:
Bully Hendry would have signed Harper for 2.5 Billion over 30 years


Top
 Profile  
 
PostPosted: Fri Jan 17, 2020 11:17 am 
Offline
User avatar

Joined: Mon Oct 03, 2005 1:04 pm
Posts: 13260
Location: God's country
pizza_Place: Gem City
Darkside wrote:
Also.... is this a carrier?

Aorrybit took so long to get back to you I'm out working.
It's an "Air Ease" Johnson (Armstrong) Ultra SX 90.

I had initially ignored the lower section since it only houses the circulation fan and that didn't seem to be a likely suspect. However, when I looked at the lower housing I found a piece of thin insulation up against the circulation fan. I assume it was supposed to be attached to the enclosure sheet metal for sound or thermal purposes, but certainly not against the fan. I am guessing this condition would be very similar to having a very clogged filter. I removed it and it seems to be operating fine.

There was also a fair amount of condensation in the exhaust drip leg which I drained.

Finally, it is an non-direct installation (no intake pipe to exterior).

Thanks to both you and Ike. It's been very informative. I'll update if the problem continues.

_________________
“Mr. Trump is unfit for our nation’s highest office.”- JD Vance
“My god, what an !diot.”- JD Vance tweet on Trump
“I’m a ‘Never Trump’ guy”- JD Vance


Last edited by Zippy-The-Pinhead on Fri Jan 17, 2020 11:53 am, edited 1 time in total.

Top
 Profile  
 
PostPosted: Fri Jan 17, 2020 11:23 am 
Offline
100000 CLUB
User avatar

Joined: Wed Feb 08, 2006 6:17 pm
Posts: 102657
pizza_Place: Vito & Nick's
whistler wrote:
Darkside wrote:
I'm out working.

at 11:30PM?
The best way for your to keep warm is to go into your garage and start your car. Just leave it running until you fall asleep.

_________________
Joe Orr Road Rod wrote:
It's more fun to be a victim
Caller Bob wrote:
There will never be an effective vaccine. I'll never get one anyway.


Top
 Profile  
 
PostPosted: Fri Jan 17, 2020 11:40 am 
Offline
User avatar

Joined: Thu Jul 13, 2006 1:25 pm
Posts: 27055
Darkside wrote:
IkeSouth wrote:
Darkside wrote:
Zippy-The-Pinhead wrote:
Darkside wrote:
Zippy-The-Pinhead wrote:
I have just been informed that our furnace is continually blowing cold air. The fan continues to run even when the thermostat it shut off. I had my wife flip of the “light switch” on the side of the furnace and that did shut off the fan. The thermostat is one of those cheap round mechanical style and the furnace is a high efficiency unit that is at least 20 years old. Of course I am in the process of flying back from Denver so I can’t view it 1st hand until this evening. I can do basic tests and repairs but obviously if this is serious it will require an expert. I’m just not sure whether to just have my wife call a technician now or hold off until I can mess with it a bit tonight. Any thoughts or suggestions (other than move)? Thanks in advance.

If the heat comes on when you turn up the stat it may be that the thermostat is sending an improper signal to the furnace to run. You can test this with a multimeter. If you have voltage between the g and the c terminal 24 volts it's probably a thermostat thing.
If the heat won't come on but the fan stays on it's likely an open limit. Either a main limit or possibly an auxiliary limit in a blower compartment. If you put your meter on both sides of the limit and it reads 0 its closed and not likely the cause. If you read 24 volts across a limit its open and that's the problem.
If it's a high efficiency it should have an error code should there be a reason other than the thermostat that's causing the issue. Before killing power to the furnace see if its throwing a code. You can update this thread with a make and model and I'll try to help.
So I had to reset the flame rollout switch. That seems to have at least temporarily solved the problem. The furnace has been running for about 1/2 an hour and the house is finally nearing “room temperature “. I also pulled the limit switch to make sure it wasn’t stuck and that solved the fan running problem. The question now is: is this a bigger concern even if it doesn’t happen again?

Thanks again btw. :salut:

Rollout switches indicate either a lack of combustion air or a bad heat exchanger typically.
So... you can take the intake pipe off the furnace and see if that helps. It could be a clogged intake pipe.
If it's a bad or rusted out secondary heat exchanger you would confirm with a combustion analysis. High co and low o2 is likely what you'd find.
One way to test an intake pipe is to drop a golf ball into the intake from outside. The pipes should be pitched toward the furnace so if the ball makes it back to the furnace that confirms the pitch is correct and the pipe is clear. Exhaust should be the same way.
Also I've seen clogged condensate traps cause this. If water is backing up into the secondary it could be enough to cause a rollout to trip but typically the pressure switch won't close before that happens but I've seen it before so I wouldn't rule it out entirely.


To check intake just run the furnace without the cover on the burner. Might have to tape down a door switch.

This will likely cause other problems. Best practice is to cut the intake pipe a foot or so away from the furnace move the pipe ends apart and leave the combustion door in place. The pipe can be put back together easily enough with a fernco or glue in a coupling.


what other problems? not arguing. i only know shitty residential furnaces through theory not a whole lot of experience

_________________
the world will always the world. your entire existence is defined by your response.


Top
 Profile  
 
PostPosted: Fri Jan 17, 2020 11:50 am 
Offline

Joined: Thu Apr 19, 2018 11:26 am
Posts: 14931
pizza_Place: Grazianos
Boilermaker Rick wrote:
Zippy-The-Pinhead wrote:
I have just been informed that our furnace is continually blowing cold air.
I think that's called an air conditioner.


Great analysis. :lol: :lol: :lol:

_________________
An Ode to the Texas man who shot an Antifa terrorist:

Oh, he might have went on livin'
But he made one fatal slip
When he tried to match the Ranger
With the big iron on his hip


Top
 Profile  
 
PostPosted: Fri Jan 17, 2020 12:01 pm 
Offline
User avatar

Joined: Wed Jun 28, 2006 9:29 am
Posts: 65791
Location: Darkside Estates
pizza_Place: A cat got an online degree.
Quote:
what other problems? not arguing. i only know shitty residential furnaces through theory not a whole lot of experience

If you look at the intakes for high efficiency systems they typically have a baffle that regulates the flow of fresh air into the system or distributes it in such and such a way.
So theres these carrier systems, and they have the air intake that goes into a black plastic fitting under the burner enclosure. It's designed with a 2 inch opening on either side so you can pick which side to bring your air into based on the design of the ductwork. The unused side has a black plastic cap.
So a coworker of mine went out to a no heat call after a decent snowfall last year. The intake was clogged in such a way that it would have to be completely cut open but it was in a ceiling of a now finished basement so the ceiling would have to be cut out.
Now I carry barometric dampers to install in such situations but apparently this guy didnt have that so he just popped the other plastic cap off. Problem solved right?
I had to go back the next day. Ignition failures, namely carryover.
So I run this thing and combustion shows 220 PPM CO and something silly like 16% O2. I popped the cap back in, ran a nerf baseball into the intake with a fish line and pushed out the compacted snow on the intake (and ultimately installed the barometric damper) and retested combustion. 23 PPM CO and 9.9% O2. So having unrestricted intake air threw off the air fuel mixture enough to create incomplete combustion and also fuck up the carryover wing on one of the burners.
Install manuals typically state in an indirect vent to put 2 feet or so of pvc in on intake side. Must be a reason for it... :wink:

_________________
"Play until it hurts, then play until it hurts to not play."
http://soundcloud.com/darkside124 HOF 2013, MM Champion 2014
bigfan wrote:
Many that is true, but an incomplete statement.


Top
 Profile  
 
PostPosted: Fri Feb 21, 2020 7:51 am 
Offline
User avatar

Joined: Mon Apr 21, 2008 7:35 pm
Posts: 18202
Location: Headed to the 19th hole
pizza_Place: Kaisers
Have water leaking out from furnace so I called someone. The furnace has a humidifier on it and it was completely caked with calcium and crud. Guy took it off and did his best to clean it. He didn’t have the right size filter to replace it. He checked a few more things and then left. I bought the filter and let it run. Still leaking. I called back, the gal puts me on hold and then comes back. She talked to the tech and he said it’s probably a corroded heat exchanger and you will likely need a new furnace. I couldn’t believe what I was hearing. Quite a turn of events. They are sending another tech this afternoon to diagnose. Even if I do need a new furnace I’m not buying it from these guys. Frustrating.

_________________
Flew too close to the sun on wings of pastrami


Top
 Profile  
 
PostPosted: Fri Feb 21, 2020 8:30 am 
Offline
User avatar

Joined: Thu May 28, 2009 11:10 am
Posts: 42094
Location: Rock Ridge (splendid!)
pizza_Place: Charlie Fox's / Paisano's
"HVAC Question for Darkside" can be sung to the tune of "Love That Chicken from Popeye's".

_________________
Power is always in the hands of the masses of men. What oppresses the masses is their own ignorance, their own short-sighted selfishness.
- Henry George


Top
 Profile  
 
PostPosted: Fri Feb 21, 2020 8:44 am 
Offline
User avatar

Joined: Mon Apr 21, 2008 7:35 pm
Posts: 18202
Location: Headed to the 19th hole
pizza_Place: Kaisers
Don Tiny wrote:
"HVAC Question for Darkside" can be sung to the tune of "Love That Chicken from Popeye's".


Not only does it fit but it was meant to be sung that way. :lol: :lol: :lol:

_________________
Flew too close to the sun on wings of pastrami


Top
 Profile  
 
PostPosted: Fri Feb 21, 2020 9:36 am 
Offline
1000 CLUB
User avatar

Joined: Fri May 13, 2005 4:47 pm
Posts: 28634
Location: computer
pizza_Place: Salerno's
and...now I want chicken.

_________________
@audioidkid
spaulding wrote:
Also if you fuck someone like they are a millionaire they might go try to be one.


Top
 Profile  
 
PostPosted: Fri Feb 21, 2020 9:51 am 
Offline
User avatar

Joined: Thu Sep 30, 2010 3:40 pm
Posts: 16490
pizza_Place: Boni Vino
T-Bone wrote:
Have water leaking out from furnace so I called someone. The furnace has a humidifier on it and it was completely caked with calcium and crud. Guy took it off and did his best to clean it. He didn’t have the right size filter to replace it. He checked a few more things and then left. I bought the filter and let it run. Still leaking. I called back, the gal puts me on hold and then comes back. She talked to the tech and he said it’s probably a corroded heat exchanger and you will likely need a new furnace. I couldn’t believe what I was hearing. Quite a turn of events. They are sending another tech this afternoon to diagnose. Even if I do need a new furnace I’m not buying it from these guys. Frustrating.


Same thing happened to me a couple months ago. Corroded secondary heat exchanger. 16 years old but covered under 20-yr warranty but does NOT include labor. $1,200 to fix vs $6k for new.

_________________
To IkeSouth, bigfan wrote:
Are you stoned or pissed off, or both, when you create these postings?


Top
 Profile  
 
PostPosted: Fri Feb 21, 2020 9:53 am 
Offline
100000 CLUB
User avatar

Joined: Wed Feb 08, 2006 6:17 pm
Posts: 102657
pizza_Place: Vito & Nick's
T-Bone wrote:
Have water leaking out from furnace so I called someone. The furnace has a humidifier on it and it was completely caked with calcium and crud. Guy took it off and did his best to clean it. He didn’t have the right size filter to replace it. He checked a few more things and then left. I bought the filter and let it run. Still leaking. I called back, the gal puts me on hold and then comes back. She talked to the tech and he said it’s probably a corroded heat exchanger and you will likely need a new furnace. I couldn’t believe what I was hearing. Quite a turn of events. They are sending another tech this afternoon to diagnose. Even if I do need a new furnace I’m not buying it from these guys. Frustrating.
Did you have a home inspection or anything done before you bought the place? Not sure if there is anything you can do seeing as how you've been there just a few months, yeah?

_________________
Joe Orr Road Rod wrote:
It's more fun to be a victim
Caller Bob wrote:
There will never be an effective vaccine. I'll never get one anyway.


Top
 Profile  
 
PostPosted: Fri Feb 21, 2020 10:09 am 
Offline
User avatar

Joined: Mon Apr 21, 2008 7:35 pm
Posts: 18202
Location: Headed to the 19th hole
pizza_Place: Kaisers
Frank Coztansa wrote:
T-Bone wrote:
Have water leaking out from furnace so I called someone. The furnace has a humidifier on it and it was completely caked with calcium and crud. Guy took it off and did his best to clean it. He didn’t have the right size filter to replace it. He checked a few more things and then left. I bought the filter and let it run. Still leaking. I called back, the gal puts me on hold and then comes back. She talked to the tech and he said it’s probably a corroded heat exchanger and you will likely need a new furnace. I couldn’t believe what I was hearing. Quite a turn of events. They are sending another tech this afternoon to diagnose. Even if I do need a new furnace I’m not buying it from these guys. Frustrating.
Did you have a home inspection or anything done before you bought the place? Not sure if there is anything you can do seeing as how you've been there just a few months, yeah?


Had a home inspection so I can go back and look at that but we didn’t have any kind of insurance built in. It’s only 9 years old so maybe this other tech will sing a different tune. I just want to know where I stand with it so I can make a decision.

_________________
Flew too close to the sun on wings of pastrami


Top
 Profile  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 53 posts ]  Go to page 1, 2  Next

All times are UTC - 6 hours [ DST ]


Who is online

Users browsing this forum: No registered users and 5 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum

Search for:
Jump to:  
Powered by phpBB® Forum Software © phpBB Group